I am working on a project which has a conveyor that has a 25hp 480V motor being fed from a 50A breaker. The motor feeders going to this motor are a
3/C #6 w/gnd. Since the motor is sitting on a stell conveyor structure I am looking at having to equipment ground the conveyor structure.
My question is, weather or not I have to look at table 250.122 and run a #10 equipment grounding conductor (using 60A overcurrent device rating from table) from the MCC to the conveyor structure. Is it possible to just use the ground wire that is running with the motor feeds and bond it to the conveyor structure or do I need a seperate equipment ground conductor for this instance.
3/C #6 w/gnd. Since the motor is sitting on a stell conveyor structure I am looking at having to equipment ground the conveyor structure.
My question is, weather or not I have to look at table 250.122 and run a #10 equipment grounding conductor (using 60A overcurrent device rating from table) from the MCC to the conveyor structure. Is it possible to just use the ground wire that is running with the motor feeds and bond it to the conveyor structure or do I need a seperate equipment ground conductor for this instance.