I have plans which show incoming service conductors from poco into utility meter /junction box and from their into main service panelboard A.
In the junction box their is neutral to ground bond and between utility meter and main service panelboard A their is #6 awg ground conductor along with phase and neutral conductors to main service panel A. Main service grounding electrode system is at junction box.
Please see attached sketch describing above.
Their is also neutral to ground bond at main service panelboard A
Question:
1. Does the NEC 2014 allow equipment grounding conductor between utility meter and main service panelboard A? I thought everything was suppose to be grounded by neutral if its grounded conductor line side service disco. Would the install not comply per NEC 2014 section 250.80?
In the junction box their is neutral to ground bond and between utility meter and main service panelboard A their is #6 awg ground conductor along with phase and neutral conductors to main service panel A. Main service grounding electrode system is at junction box.
Please see attached sketch describing above.
Their is also neutral to ground bond at main service panelboard A
Question:
1. Does the NEC 2014 allow equipment grounding conductor between utility meter and main service panelboard A? I thought everything was suppose to be grounded by neutral if its grounded conductor line side service disco. Would the install not comply per NEC 2014 section 250.80?