equipment ground conductor 2008 nec

Status
Not open for further replies.

grumpy11

Senior Member
im pulling an equipment ground conductor from a new switch to an existing pull box to re feed existing. the new egc i want to pull is per article 250.122 hence the existing egc does not match. is this a code violation to splice a larger egc to a smaller one
 
equipment ground conductor

equipment ground conductor

no im putting in a 1/0 for 800 amps and the existing is #2
 
OK, so in other words you want to extend the existing feeder which has an undersized EGC. Is this in a raceway, what's the setup?
 
If I understand, you are re-feeding an 800 amp circuit up to an existing point and leaving the rest of the circuit as is. The existing EGC was too small to start with.

I believe you are doing the right thing by using properly sized EGC for the new portion. As far as the existing portion, it was wrong to start with, and the issue is not clear as to whether or not you should do anything with what portion was existing. I say if it is easy to replace then by all means replace it. Chances are it may not be a simple fix otherwise you may not be asking.

One simple fix would be if you have a qualifying metallic raceway to use as the EGC, then all you need to do is disconnect the existing conductor.
 