I'm involved in rebuild of a customer owned industrial sub that has a 13.2kV feeder from secondary of substation down to the plant's main incoming switchgear. Utility metering is on primary of substation transformer so everything from transformer down falls under NEC purview in my opinion.
The 13.2kV feeder from the sub will be underground cable before it transitions to a new short overhead line to join an existing overhead (ASCR cable) line that is run into the existing facility.
Am I correct in understanding that the NEC requires a separate EGC and thus my new OH line portion will need to have a ground wire (UG portion of cable will have an EGC run up to pole)? In these cases is the OH ground typically installed as a shield above ASCR phase conductors, or below it similar to a utility Distibution neutral?
It also appears that the existing OH line going into the plant does not have any sort of separate EGC? This was a much older installation and at one point in time looks like system may have been LRG grounded (its solidly grounded now). Is there any sort of exception in NEC for older installations that did not have an EGC? Is there an approach to a situation like there where one does not exist for OH cables traversing several hundred yards before getting to facility?
The 13.2kV feeder from the sub will be underground cable before it transitions to a new short overhead line to join an existing overhead (ASCR cable) line that is run into the existing facility.
Am I correct in understanding that the NEC requires a separate EGC and thus my new OH line portion will need to have a ground wire (UG portion of cable will have an EGC run up to pole)? In these cases is the OH ground typically installed as a shield above ASCR phase conductors, or below it similar to a utility Distibution neutral?
It also appears that the existing OH line going into the plant does not have any sort of separate EGC? This was a much older installation and at one point in time looks like system may have been LRG grounded (its solidly grounded now). Is there any sort of exception in NEC for older installations that did not have an EGC? Is there an approach to a situation like there where one does not exist for OH cables traversing several hundred yards before getting to facility?