For MV or LV systems that are fed from a ungrounded delta secondary are there any grounding requirements for EGC's or ground wires to be run with the phase conductors similar to what you would have with a grounded system?
I understand that ungrounded delta systems will not have any fault current flow for a L-G fault and thus no need for an EGC, but I wanted to make sure that I'm not missing anything in the NEC that requires a ground to be run with the phase conductors. The way I see it just the phase conductors will be run between the transformer secondary and the first disconnecting means. Is this correct?
I understand that ungrounded delta systems will not have any fault current flow for a L-G fault and thus no need for an EGC, but I wanted to make sure that I'm not missing anything in the NEC that requires a ground to be run with the phase conductors. The way I see it just the phase conductors will be run between the transformer secondary and the first disconnecting means. Is this correct?