I have (6) parallel feeds of 3/c 500MCM per phase coming off of a three phase 480V 2000A rated breaker (off secondary of xfmr) feeding a 480V MCC. My question concerns what size equpment ground conductors need to be run with each of the (6) parallel feeds?
Per 250.122(F) I understand that as saying that each equipment ground conductor run with each of the (6) 3/c feeders needs to be rated for the rating of the overcurrent device which in this case is 2000A. Looking at table 250.11 the size of the EGC corrosponding to 2000A is 250MCM. I am understanding this to mean that each of the (6) ECG in this parallel feed needs to be 250MCM or greater. Is this correct?
What if I had a similar situation where I had the same circuit going between the low side of a transformer over to a piece of switchgear which contained a main breaker (15ft) ? There is no overcurrent device directly on the transformer so what would I use as the overcurrent device rating in this case to corrospond to 250.122?
Per 250.122(F) I understand that as saying that each equipment ground conductor run with each of the (6) 3/c feeders needs to be rated for the rating of the overcurrent device which in this case is 2000A. Looking at table 250.11 the size of the EGC corrosponding to 2000A is 250MCM. I am understanding this to mean that each of the (6) ECG in this parallel feed needs to be 250MCM or greater. Is this correct?
What if I had a similar situation where I had the same circuit going between the low side of a transformer over to a piece of switchgear which contained a main breaker (15ft) ? There is no overcurrent device directly on the transformer so what would I use as the overcurrent device rating in this case to corrospond to 250.122?