Will A GFCI receptacle trip correctly without a Equipment grounding conductor. I used Code article 406-d2 (c) and the GFCI will not trip? I must be doing something wrong?
The test button inside the GFCI receptacle itself uses a resistor to bypass current from the hot on the load side to the neutral on the line side. No current needs to flow in the EGC.Test button with a load?
That is what plug in GFCI testers do, put a load (at least 6 mA) from hot to ground. OP has no ground therefore no complete circuit for any current to flow, GFCI responds to current not voltage.Test button with a load?
And an Inspector would shoot it down ..Thus, the correct response is that a GFCI does not need an EGC to operate, but a plug-in tester does.
Then you have an opportunity to educate the inspector. There is no basis in this situation for the inspector to reject it.And an Inspector would shoot it down ..
ok then ..There is no basis in this situation for the inspector to reject it.
Until I learned here that the only way to ’test’ was the button, that was what I did with about all GFCIs. That and TR devices.A test the inspector could observe would be to use a solenoid tester between the receptacle hot and the ground of an extension cord that is plugged into a grounded receptacle. I've even used plumbing to test against when there's no EGC handy.
There are many ways to test. Only one method recognized by instructions.Until I learned here that the only way to ’test’ was the button, that was what I did with about all GFCIs. That and TR devices.
I should have inserted a' ' in "the only way to ...."There are many ways to test. Only one method recognized by instructions.
If introducing real fault current doesn't trip it, chances are the test button won't either. If it does, my suspicions go way up as to whether it is a counterfeit device or not.
A GFCI does not care if there is an equipment ground or not. It looks at the difference in current between the line and neutral (for a 120V circuit) and trips if the difference exceeds 5 mA.Will A GFCI receptacle trip correctly without a Equipment grounding conductor. I used Code article 406-d2 (c) and the GFCI will not trip? I must be doing something wrong?