I make it that you need to run 2/0 AL EGC in each raceway. Since you planned to run 4/0, you meet the minimum requirements.
The math:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Minimum for 400 amps = two sets of 250 AL</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">You are running two sets of 350 AL</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">350 / 250 = 1.4 (i.e., a 40% increase in size)</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Minimum EGC is #1 AL (83,690 circular mils)</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">1.4 times 83690 = 117,166 circular mils</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">The smallest cable that is at least 117,166 cm is #2/0</font>
<font size="2" face="Verdana, Helvetica, sans-serif">