hardworker
Senior Member
I came across some work done by an "ole-timer" electrician, that has since passed.
I found a receptacle outlet in a commercial building, 120vt, 20amp circuit, awg12, emt with no equipment ground. Just black and white conductors. It was installed prior to 1960, so green ground conductors were not in use at that time.
I was told a computer monitor was used in that outlet years ago and it was having problems due to no ground.
I was told the "ole timer" did some work on the outlet to fix the problem.
I found he had tied the neutral (white) not only to the neutral terminal on the outlet, but also looped it to the equipment ground (green) terminal. He tied the neutral to the equipment ground. Keep in mind this outlet was on EMT.
Is there any reasoning behind this? Do you think he fixed the grounding problem for the monitor? To me this is against all principals and codes.
Please give me your thoughts.
I cleaned the whole issue up by running new wiring.
I found a receptacle outlet in a commercial building, 120vt, 20amp circuit, awg12, emt with no equipment ground. Just black and white conductors. It was installed prior to 1960, so green ground conductors were not in use at that time.
I was told a computer monitor was used in that outlet years ago and it was having problems due to no ground.
I was told the "ole timer" did some work on the outlet to fix the problem.
I found he had tied the neutral (white) not only to the neutral terminal on the outlet, but also looped it to the equipment ground (green) terminal. He tied the neutral to the equipment ground. Keep in mind this outlet was on EMT.
Is there any reasoning behind this? Do you think he fixed the grounding problem for the monitor? To me this is against all principals and codes.
Please give me your thoughts.
I cleaned the whole issue up by running new wiring.