I would like your opinion on the following statement.
Section 250.142(A) permits the use of grounded circuit conductor for grounding equipment on the supply side of the service in three locations:
(1) On the supply side or within the enclosure of the ac service-disconnecting means
(2) On the supply side or within the enclosure of the main disconnecting means for separate buildings as provided in 250.32(B)
(3) On the supply side or within the enclosure of the main disconnecting means or overcurrent devices of a separately derived system where permitted by 250.30(A)(1)
One and two does permit the equipment grounding and the grounded conductors to terminate on the same buss.
The third location being on the secondary side of a separately derived system the equipment grounding conductors are required to be terminated on a separate buss, which is bonded to the grounded conductor by the system bonding jumper.
Section 250.142(A) permits the use of grounded circuit conductor for grounding equipment on the supply side of the service in three locations:
(1) On the supply side or within the enclosure of the ac service-disconnecting means
(2) On the supply side or within the enclosure of the main disconnecting means for separate buildings as provided in 250.32(B)
(3) On the supply side or within the enclosure of the main disconnecting means or overcurrent devices of a separately derived system where permitted by 250.30(A)(1)
One and two does permit the equipment grounding and the grounded conductors to terminate on the same buss.
The third location being on the secondary side of a separately derived system the equipment grounding conductors are required to be terminated on a separate buss, which is bonded to the grounded conductor by the system bonding jumper.