A three phase 4-wire service consists of three 600 kcmil conductors per phase and installed in three PVC conduits. The local inspector is insisting on a 3/0 equipment grounding conductor in each conduit.
While most of us would agree that the EGC is not required, and that it violates 310.4(B) because it would be paralleled with the neutral, does anyone know of any specific language that could be used to convince the inspector the the EGC is not required in a service raceway?
Using 310.4(B) is shakey because he may require a 600 kcmil EGC to avoid the violation.
Thanks,
Brian Dolan