vick67
Member
- Location
- United States
That is a supply side bonding jumper and is sized per Table 250.66 or the 12.5% rule for where the largest phase conductor exceeds 1100 kcmil.Sorry Gary I meant to say between the ground in the transformer and the ground in the first panel.
Thanks,
Chad
It stays a supply side bonding jumper until the circuit has overcurrent protection. At that point the conductors become feeders or branch circuits and you install an EGC sized per 250.122.Thanks Don. If this panel had feed thru lugs to a second panel then the supply side bonding jumper wire size would remain constant until all panels are bonded is the way I see it.