equipment grounding conductor placement

Status
Not open for further replies.

madmike

Member
On a derived system, should the primary circuit equipment grounding conductor be landed anywhere other than the cabinet. That is, should/must it be kept off the ground bar and or the X0 terminal?
Thanks.
 
I think what you are asking is if the EGC ran with primary circuit conductors is allowed to connect to the chassis of the xfmr and no where else, this is not the case. Since you must re-bond the separately derived system the "primary" EGC will be connected to X0, the xfmr chassis, neutral & ground bus, derived system GES via the system bonding jumper. This ties everything back together at the newly derived system, it is kind of like starting over. The secondary side is electrically isolated from the primary and a new neutral is being derived this is not making another ground/neutral connection on the load side of the service.
 
On a derived system, should the primary circuit equipment grounding conductor be landed anywhere other than the cabinet. That is, should/must it be kept off the ground bar and or the X0 terminal?
Thanks.

It should be kept off of XO if you plan on installing the system bonding jumper in the panelboard. I always land it on the cabinet of the xfmr regardless of where the system bonding jumper is installed.
 