mfranklin
Member
- Location
- Littleton, CO
I'm currently working on a project where we have a 4000A incoming service with 13 parallel runs of 4-500MCM AL and 1-500MCM AL equipment ground. The inspector is stating per Table 250.122 that equipment ground must be a 750MCM AL. The engineer of record and us are saying that per 250.122(A) the equipment grounding conductor does not have to be larger than the circuit conductors supplying the equipment. Thoughts?