Equipment Grounding Conductor Technical Interpretation

Status
Not open for further replies.

Dane Clarke

New member
Mike,

Re: Technical Interpretation

I am writing to you in order to get a technical interpretation regarding the following scenario:

Facility Description:

On a campus, there is a 115kV/13.8kV primary substation, 140MVA, which is fed from a 115kV overhead utility line. The metering is in 115KV. The 115kV/13.8kV primary substation feed several buildings throughout the campus at 13.8 KV with several 13.8kV/480V secondary substations in each building.

Grounding Equipment Conductor Questions:

1. Are the feeds coming from the 115kV/13.8kV primary substation, which supply the 13.8kV/480V secondary substations considered to be a service or a feeder?
2. Some of the existing feeders are in a duct bank with a common bare 4/0 CU conductor embedded in the top of the duct bank. It is an Equipment Grounding Conductor (EGC) required for each 13.8 KV feeder or the common ground would be enough?
3. If so, does the Equipment Grounding Conductor (EGC) have to be insulated?
 
First of all, Mike very seldom posts any replies on his own forum. Secondly, those of us who do participate cannot provide any "technical interpretations." All we can offer is our own individual opinion. Third, my opinions are (1) Feeders, (2) Common is good enough, and (3) No.

Welcome to the forum.
 
Charlie,
For your answer to Q2, are you assuming that 300.3(B)(3) applies? If not, what permits a single EGC for this installation?
 
Charlie,
For your answer to Q2, are you assuming that 300.3(B)(3) applies? If not, what permits a single EGC for this installation?
Perhaps such starts with...
300.2 Limitations.
(A) Voltage. Wiring methods specified in Chapter 3 shall
be used for 600 volts, nominal, or less where not specifically
limited in some section of Chapter 3. They shall be
permitted for over 600 volts, nominal, where specifically
permitted elsewhere in this Code.
 