I recently looked at an installation of a portable at a school. This particular job is really bugging me because after much time and research I have not been able to answer a question to my satisfaction. Three phase 480 volt with equipment grounding conductor in non-metallic raceway ran from an existing panel in the school to an OUTSIDE transformer. Equipment grounding conductor is bonded to transformer frame. Secondary is 208/120 volt; three ungrounded conductors & the grounded conductor with NO equipment grounding conductor; again non-metallic raceway to a 200 amp panel in the portable. The secondary conductors are located outside until they enter the back of the panel. Panel at portable is bonded with main bonding jumper and a grounding electrode system was installed (just like a new service).
Here is my problem. Is the equipment grounding conductor required with the secondary conductors? A short circuit at the portable would not be cleared by the primary overcurrent protection but the secondary conductors are protected by the 200 amp breaker where they terminate at the portable. Another issue I have is the fact that there are low voltage system installed between the school and new portable. In my opinion there is a difference in potential between the low voltage systems ground and the new line voltage ground established at the portable. There is not a complete line voltage equipment ground from the school to the portable.
Is it a code violation NOT to have the equipment grounding conductor ran with secondary? Would another solution be to bond the grounded conductor(x0) again at the transformer, using the grounded conductor also as the equipment ground? This seems to be a situation where this would be compliant with the code. Thanks for any help.
Here is my problem. Is the equipment grounding conductor required with the secondary conductors? A short circuit at the portable would not be cleared by the primary overcurrent protection but the secondary conductors are protected by the 200 amp breaker where they terminate at the portable. Another issue I have is the fact that there are low voltage system installed between the school and new portable. In my opinion there is a difference in potential between the low voltage systems ground and the new line voltage ground established at the portable. There is not a complete line voltage equipment ground from the school to the portable.
Is it a code violation NOT to have the equipment grounding conductor ran with secondary? Would another solution be to bond the grounded conductor(x0) again at the transformer, using the grounded conductor also as the equipment ground? This seems to be a situation where this would be compliant with the code. Thanks for any help.