On a job that is replacing a 4 pole ATS with a 4 pole Manual Transfer switch (MTS). The existing install had conduits that went from 1600 main breaker to ATS, and return conduits that went back to load side busbar within the same switchgear to feed two feeders via 2- 800A breakers.
We abandoned the in ground conduits, and piped in 8 4" GRC runs between the switchgear and the new MTS. The line will utilize 4 conduits, and the load in the remaining 4 conduits. We are pulling 4 parallel runs of 600kcmil, to feed line side and 4 back to the load side.
My question, we used Myers hubs to make connections between MTS and Main Switchgear. The distance between MTS And Main switchgear is 48". So do I still need to run an equipment ground in every single conduit? I believe I do, but just seems redundant mostly because of the short distance between the two cabinets.
We abandoned the in ground conduits, and piped in 8 4" GRC runs between the switchgear and the new MTS. The line will utilize 4 conduits, and the load in the remaining 4 conduits. We are pulling 4 parallel runs of 600kcmil, to feed line side and 4 back to the load side.
My question, we used Myers hubs to make connections between MTS and Main Switchgear. The distance between MTS And Main switchgear is 48". So do I still need to run an equipment ground in every single conduit? I believe I do, but just seems redundant mostly because of the short distance between the two cabinets.