equipment grounding conductor

Status
Not open for further replies.

k d

Member
Location
Oklahoma
If I am feeding a 30 amp 480 volt single phase load from a two pole 30 amp breaker that is 850 feet from source to load and using #3 thhn for my ungrounded conductors (due to voltage drop) what size wire would the NEC require for the equipment gound conductor?
 
Re: equipment grounding conductor

In this case you would have to use a #3, see 250.122(B)

Roger
 