infinity said:Why would ambient temperature correction of the ungrounded conductors change the size of the EGC?
I read this as meaning for any reason.250.122(B) Increased in Size. Where ungrounded conductors are increased in size, equipment grounding conductors, where installed, shall be increased in size proportionately according to the circular mil area of the ungrounded conductors.
chris kennedy said:I read this as meaning for any reason.
inspector141 said:The equipment grounding conductor must be increased proportionally to the increase of the ungrounded conducor for the ambient temp increase. NEC 250.122(B). Use table 8 for conductors 4/0 and smaller to apply the proportional increase to the ground conductor.
Pierre C Belarge said:So the question begs, prior to the 2008 NEC, is it a requirement to adjust for ambient temperature?
Pierre C Belarge said:Just looking for some takers on this question.
Pierre C Belarge said:So the question begs, prior to the 2008 NEC, is it a requirement to adjust for ambient temperature?
chris kennedy said:OK, my 05 has adjustment factors under T310.16. Are you thinking roof tops in the 08?
Help me understand your point, Pierre. Is it a requirement to adjust WHAT for ambient temperature?Pierre C Belarge said:So the question begs, prior to the 2008 NEC, is it a requirement to adjust for ambient temperature?
charlie b said:Not to ignore your question, Pierre, but as to the original question, no, you do not derate the EGC. Never. It does not happen; we do no such thing. Did I say no yet? Nope. Nada. Niet.
Any takers on this challenge? Anyone notice that this is essentially a challenge? :smile:
No, it is not derating. You are on the right track, however.frizbeedog said:If you have to increase the size of a conductor for the load due to derating and are increasing the grounded conductor, is that not derating?
charlie b said:
No, it is not derating. You are on the right track, however.
Granted, but if you derate the ungrounded conductors then the EGC is also increased as per 250.122(B). So in a round about way, derating effects the EGC.charlie b said:you do not derate the EGC. Never. It does not happen; we do no such thing. Did I say no yet? Nope. Nada. Niet.
chris kennedy said:Granted, but if you derate the ungrounded conductors then the EGC is also increased as per 250.122(B). So in a round about way, derating effects the EGC.
True. But the OP asked about derating the EGC.chris kennedy said:. . . .So in a round about way, derating affects the EGC.