Is there ever an application where PVC conduit does not have to contain an equipment grounding conductor?
Please sight the code reference.

Thanks
 
Re: Equipment Grounding Conductor

Only place I can think of is a feeder to a seperate structure under certain conditions of 250.32 (B) where no metallic objects exist between the two structures.