I am replacing a 3000 amp lateral to an overhead. Will be installing a 3000 amp breaker outside, which will make this my new service entrance and the existing 3000amp, a feeder. Will size ground per 250.122(400MCM) From my understanding for the 8 parallel feeders metal conduit (3-500MCM) This will need to be in each conduit (250.122F1). And since this is in a raceway and not multiconductor cable the ground fault on this breaker will not apply to reduce the size (250.122F2)To not have to upsize my 3" conduit for this size of ground I am going to use the conduit as equipment ground. Are there any exceptions or any other sections that would allow sizing this smaller?