Remember that a flexible metal raceway must have overcurrent in front therefore a flexible conduit would require a conductor.
(5) Listed flexible metal conduit meeting all the following conditions:
b. The circuit conductors contained in the conduit are protected by overcurrent devices rated at 20 amperes or less.
(6) Listed liquidtight flexible metal conduit meeting all the following conditions:
b. For metric designators 12 through 16 (trade sizes 3⁄8 through 1⁄2), the circuit conductors contained in the conduit are protected by overcurrent devices rated at 20 amperes or less.
c. For metric designators 21 through 35 (trade sizes 3⁄4 through 11⁄4), the circuit conductors contained in the conduit are protected by overcurrent devices rated not more than 60 amperes and there is no flexible metal conduit, flexible metallic tubing, or liquidtight flexible metal conduit in trade sizes metric designators 12 through 16 (trade sizes 3⁄8 through 1⁄2) in the grounding path.