I know we need to increase the EGC size due to voltage drop.
For example. 50A OCPD need to have #8 per phase and #10 CU G. If we upsize the conductor from #8 to #3/0 due to voltage drop,
then 85.01 (the size of a #3/0 AWG conductor) ÷ 8.367 (the size of a 8 AWG conductor) = 10.16,
5.261 (the size of a 10 AWG conductor) x 10.16 (the ratio found above) = 53.45
then we need #1/0 CU G.
Question: we know 200A OCPD only need #6 CU. G per table250.122. if we change the 50A OCPD to 200A OCPD with #3/0 per phase in the example above, other condition stay same (include the load) . then the EGC will #6.
in this case, do we use #1/0 as EGC or #6 as EGC? Why?