mull982 said:
Located by the equipment will be a portable skid that has both 4160V and 480V switchgear. The switchgear on the skid will be fed from stationary switchgear in our plant so this feed will have a ground as well as a ground check monitor. Can I equipment ground all of my portable equeipment by running ground conductors from the ground bus of my switchgear on the portabe skid, as well as ground the skid from this switchgear sitting on it?
I understand that you have 4160 sharing a skid with switchgear that is 480V fed from your plant switchgear, then the individual conveyor motors distribute from the switchgear on skid, probably an MCC. If the skid is a duel fed service then notice 250-24(A)(3). To qualify your installation you really need to back up to the source and the same time keeping in mind what the destination needs.
The feed from your plant can be one of the three following:
1) 4w feeder: A, B, C, N -- if it?s a grounded system -- with a common neutral/grounded conductor as qualified in 250-32(B)
(2) by NOT having an equipment grounding conductor (EGC) or conductive path from its supply. In other words the neutral bonds to the equipment grounding and the neutral is used in a
duel purpose of ground fault path as well as current return path, but only if it not paralleling. This is the same set up as if this were a service disconnect. You will also need an electrode at the skid (250-50) with an electrode conductor at least size #6cu (250-66(A))
2) 4w feeder: A, B, C, N, & EGC -- if it?s a grounded system -- (EGC may be a conductor sized from 250-122, or it may be mechanical from 250-118, or both). This neutral/grounded conductor is qualified in 250-32(B)
(1) by HAVING an EGC or conductive path from its supply. In other words the neutral is NOT common or bonded to equipment grounding and is used in the
single purpose of current return path only because in this case it would be dangerously paralleling. Sub panels are often fed this way (250-24(A)(5)). You will also need an electrode at the skid (250-50) with an electrode conductor at least size #6cu (250-66(A))
3) 3w feeder: A, B, C, & EGC -- if its an ungrounded system -- (EGC may be a conductor sized from 250-122, or it may be mechanical from 250-118, or both). An ungrounded system is only used to disable ground fault protection for critical machinery by allowing one short to remain (that must annunciate/alarm for repair) but a second short would initiate the ground fault protection (open the circuit). Again these are used typically industrially for
critical machinery qualified as being dangerous if it faults and stops. An ungrounded system is one that does not have a grounded conductor from the source, you cannot have an ungrounded system from a grounded system (wye) unless you route through another separately derived system like a transformer; conversely to this you cannot have a grounded system from an ungrounded system unless you route through another separately derived system like a transformer. You will also need an electrode at the skid (250-50 & 250-32 (C)) with an electrode conductor at least size #6cu (250-66(A))
mull982 said:
Each piece of equipment will have a 480V motor on it which will have a ground along with its feeders. Is it possible to use the ground wire that is pulled to the motor and bond this to the piece of equipment (conveyor) on which the motor sits?
Absolutely, this is the purpose of the equipment grounding conductor (EGC) that is with the circuit to the motor; this enables an effective ground fault path 250-4(A)(5), you do need to make sure you have an true fault path from motor (destination) to source (ultimately XO of a transformer or gen set neutral/grounded conductor).
Keep this clich? in mind: shorts do not go to ground (earth), shorts only try to return to source and they do this through bonding!
Rods do not provide any ground fault protection and they do not give you a safer installation for this purpose. The only reasons for ground rods are described in 250-4(A)(1), ?Electrical System Grounding. Electrical systems that are grounded shall be connected to earth in a manner that will
limit the voltage imposed by lightning, line surges, or unintentional contact with higher-voltage lines?
If you have multiple motors on one conveyor you only need to bond it once according to the largest circuit and use table 250-122 to size it. If you?re using cable or cord for each motor branch circuit and it already includes EGC bond them as well. Notice this picture for a visual of effective ground fault path: