equipment grounds in juction boxes

Status
Not open for further replies.

recatirmc

New member
what is the requirement for grounding jboxes with splices and can the race- way be considered a means of ground from jbox to jbox.also can a bonding bushing be used in replace of ground screw
 
In general the EMT or metallic raceway can be considered an effective ground, however certain applications call for an insulated copper EGC (critical Care areas, etc).

I guess it depends on your application.


can a bonding bushing be used in replace of ground screw?

A ground screw would not necessarily be needed if you are running metallic raceway. Where are you planning to bond the bushing to-- from the pipe to the box???? If yes, you still need the ground screw. I don't believe a bonding bushing is an alternative to a ground screw--- they serve different purposes.
 