408.41 Grounded Conductor Terminations. Each grounded
conductor shall terminate within the panelboard in an individual
terminal that is not also used for another conductor.
Exception: Grounded conductors of circuits with parallel conductors
shall be permitted to terminate in a single terminal if the terminal is
identified for connection of more than one conductor.
thanks, thought so!
At first glance when looking at the panel, I thought it was a neutral but it is an equipment ground that is installed. This photo is deceiving !!
"If it is a grounded conductor then it needs to land on the neutral buss bar."
Is that true even in the Main Breaker Panel? example adding a grounding bar for more flexibility and then someone comes along terminating a neutral under one the the grounding bar terminals.
In most Northern Virginia counties, they won't let you mix different sizes of wire either. Makes sense to me on solid conductors because the possibility of the smaller conductor could be loose, I don't think stranded would be a problem but they don't let you mix sizes.In most cases the panels are rated for 2 conductors per terminal however you cannot have a neutral (grounded conductor) doubled or a neutral and an equipment grounding conductor together as shown
The grounded conductor can not rely on the cabinet for continuity, see 200.2(B), the EGC can.Probably not if it is in fact the Main service panel with main breaker and branch and also a bonded. Adding a neutral bar by just securing it to the metal of the box does not make a neutral bar. You need to have it wired to the neutral as you could have a high impedance connection and I don't know the current capacity of a 10-32 screw or sheet metal screw for that matter.
If it is a sub panel with isolated neutral bar then no.
In most Northern Virginia counties, they won't let you mix different sizes of wire either. Makes sense to me on solid conductors because the possibility of the smaller conductor could be loose, I don't think stranded would be a problem but they don't let you mix sizes.
Sent from my SM-T350 using Tapatalk
Much to the chagrin of many, always (provided the neutral is the grounded conductor... which isn't always true). The electrical demarcation is the Main Bonding Jumper. Grounded conductors to the supply side. Grounding conductors to the other side."If it is a grounded conductor then it needs to land on the neutral buss bar."
Is that true even in the Main Breaker Panel? example adding a grounding bar for more flexibility and then someone comes along terminating a neutral under one the the grounding bar terminals.
Still works that way when grounded conductor is not a neutral though.Much to the chagrin of many, always (provided the neutral is the grounded conductor... which isn't always true). The electrical demarcation is the Main Bonding Jumper. Grounded conductors to the supply side. Grounding conductors to the other side.
Probably not if it is in fact the Main service panel with main breaker and branch and also a bonded. Adding a neutral bar by just securing it to the metal of the box does not make a neutral bar. You need to have it wired to the neutral as you could have a high impedance connection and I don't know the current capacity of a 10-32 screw or sheet metal screw for that matter.
If it is a sub panel with isolated neutral bar then no.