Equipment load, or branches within equipment?

Status
Not open for further replies.

fifty60

Senior Member
Location
USA
I know working backwards from the load until I see the first disconnect device is my Branch Circuit. But what about the branch loads within the equipment?

For example, I have two refrigeration compressors and a heater load all contained within the same piece of equipment. I know the compressors are both on separate branches and have there on OCPD. The same for the Heater, it is on its own branch protected by its own OCPD.

The equipment as a hole also has a line of site fused disconnect. So working back from the load, if I consider the equipment as a hole to be the load, then the feeder is everything from the line of sight disconnect to the equipment. I get confused when I consider the branches within the equipment. Since inside the equipment I break out into different branches, would I have to consider from the load to the line of site disconnect to be a feeder?
 
It sounds to me like the branch circuit begins at the fused disconnect. The devices internal to the equipment would be "supplementary overcurrent devices." But take a look at the article 100 definition of that phrase, and let me know if you agree.
 