Equipment near hot tub
The Disconnect For The Ac Which Is A Switching Device Shall Be At Least 5' Horizontally From The Inside Wall Of The Spa. Art 680.22 (b) (5) O5 Nec. The Ac Shall Be Bonded To The Spa With A Solid # 8 Cu. Art. 680.26 (b) (5) (1)
Good place to set an aluminum can of cold beer??? and hope to God the AC is at the same potential as the water you are soaking in.
I went thru 680 a couple of times and came to the same conclusion bond it or separate it with a permanent barrier.
Am I missing something?
Switching Devices Shall Be Located At Least 5' From Inside Walls Or Separted From Spa By A Permanent Barrier. Art 680.22 (c). I Used Art 680.22 (b) (5) In My First Reply Looked At One Paragraph And Typed Another.