overkill94
Member
- Location
- California
Regarding overcurrent protection for an individual piece of equipment (i.e. CNC lathe), NEC section 409.21 is a bit confusing for me.
I've called out fuses provided with a piece of equipment as being oversized (i.e. 200 Amp fuses provided with a piece of equipment rated at 80 Amps and the upstream circuit breaker also being 200 Amps) and gotten some pushback from the manufacturer. They maintain that as long as each branch circuit is properly protected then it doesn't really matter what the main overcurrent protection is as long as it properly protects the incoming wiring (which makes sense to me).
Am I misreading this section or should a calculation be made for every piece of equipment as far as overcurrent protection is concerned?
I've called out fuses provided with a piece of equipment as being oversized (i.e. 200 Amp fuses provided with a piece of equipment rated at 80 Amps and the upstream circuit breaker also being 200 Amps) and gotten some pushback from the manufacturer. They maintain that as long as each branch circuit is properly protected then it doesn't really matter what the main overcurrent protection is as long as it properly protects the incoming wiring (which makes sense to me).
Am I misreading this section or should a calculation be made for every piece of equipment as far as overcurrent protection is concerned?