rotmgbetter
Member
- Location
- Houston, Texas
- Occupation
- Researcher
Hi,
I have a customer owned transformer at 12,470 WYE to 480/277 with 175 amps on the primary side and 4500 amps on the secondary. The utility proposed installing either an utility owned or customer owned recloser as the means of overcurrent protection. I was wondering exactly how I can repurpose this as the service disconnect such that I do not need an additional MV disconnect.
Is there any MV reclosers that are electronically controlled and can be manually operated from the ground to satisfy the NEC requirement of being a "readily accessible" disconnect?
Thank you
I have a customer owned transformer at 12,470 WYE to 480/277 with 175 amps on the primary side and 4500 amps on the secondary. The utility proposed installing either an utility owned or customer owned recloser as the means of overcurrent protection. I was wondering exactly how I can repurpose this as the service disconnect such that I do not need an additional MV disconnect.
Is there any MV reclosers that are electronically controlled and can be manually operated from the ground to satisfy the NEC requirement of being a "readily accessible" disconnect?
Thank you