I am requesting help(or conformation)that I am doing my first multi-motor/combination equipment correctly.
The outdoor unit for a multi fan, multi (staged) compressor commercial AC unit says:"CMA (Circuit minimum amps)114.38 amps and CMOP (Circuit maximum overcurrent protection) 150 amps.
430.25 "conductor ampacity not less than marked MCA".
(2 RLA and 2 FLA add to about 96 amps.)
Do I use the 114 with no factors (#2 THHN) beause the manufacturer already factored or do I 115% or 125% this number? (I think not, please confirm)
Thanks