The NEC requires equipment that will be interrupting fault current, have an adequate interrupting rating (110.9).
Is there any code requirement for equipment that doesn't switch, to have an adequate withstand rating.
For example, a #14 THHN conductor has a withstand rating/curve, which represents the conductors ability to withstand fault current for a period of time before failure.
A safety switch has a withstand rating for the same reason.
I am discussing the same concept with a static switch manufacturer, where the switch will not require an interrupting rating, since it doesn't attempt to interrupt a fault, but will be called upon to withstand the fault if it should occur. They feel that a withstand rating is not required by any code. It seems weird to me that there not be a withstand rating.
Is there any code requirement for equipment that doesn't switch, to have an adequate withstand rating.
For example, a #14 THHN conductor has a withstand rating/curve, which represents the conductors ability to withstand fault current for a period of time before failure.
A safety switch has a withstand rating for the same reason.
I am discussing the same concept with a static switch manufacturer, where the switch will not require an interrupting rating, since it doesn't attempt to interrupt a fault, but will be called upon to withstand the fault if it should occur. They feel that a withstand rating is not required by any code. It seems weird to me that there not be a withstand rating.