Ken9876
Senior Member
- Location
- Jersey Shore
I have a question on the location of the EGC, is there a spot at the service where it should or should not originate from? I have this job where a service switch was installed, but they used a fused disconnect for the switch. The neutral is not bonded to that switch which I see as one big problem. Then the conductors feed into the meter pan where the EGC is bonded to the service neutral, From the meter pan the 277/480 volt feed runs to the building about 300? away, into a main breaker. The neutral and EGC are separate at that location, which I feel is correct because the OCPD for the service was at the meter pan so the conductors running up the building become feeders and the neutral and EGC should be separate. But the EGC coming from the meter pan seems odd.