Equipotential bonding between HV Utility Sub grid and plant underground “loop”

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
We have a utility HV substation that is probably 50 feet from an industrial plant which employs an equipotential plane (buried ground “loop” of bare 4/0 cable)
The HV substation has its own buried grid installed per IEEE 80. There are HV feeders extending underground from the substation to transformers in the plant. The cables are shielded. The upstream delta-wye HV transformers in the substation have neutral grounding resistors that limit the amps on ground fault until the breaker trips via protective relaying (shielding should carry the fault)
Is it necessary to tie the two underground bonding systems together?


Sent from my iPhone using Tapatalk
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
It seems to me that the NEC does not cover this kind of thing. Therefore, it would not appear to come under the purview of an inspection agency but rather the utility.
 

Dale001289

Senior Member
Location
Georgia
We have a utility HV substation that is probably 50 feet from an industrial plant which employs an equipotential plane (buried ground “loop” of bare 4/0 cable)
The HV substation has its own buried grid installed per IEEE 80. There are HV feeders extending underground from the substation to transformers in the plant. The cables are shielded. The upstream delta-wye HV transformers in the substation have neutral grounding resistors that limit the amps on ground fault until the breaker trips via protective relaying (shielding should carry the fault)
Is it necessary to tie the two underground bonding systems together?


Sent from my iPhone using Tapatalk
In my opinion this sort of equipotential bonding between the two is not required. The SS has its own electrode system and so does the downstream facility. Whats important is the fault path via the cable shielding back to the source at the SS. Check number of cycles before protective relaying trips via the cable shielding to ensure the cable itself is not damaged.
 