Isaiah
Senior Member
- Location
- Baton Rouge
- Occupation
- Electrical Inspector
We have a utility HV substation that is probably 50 feet from an industrial plant which employs an equipotential plane (buried ground “loop” of bare 4/0 cable)
The HV substation has its own buried grid installed per IEEE 80. There are HV feeders extending underground from the substation to transformers in the plant. The cables are shielded. The upstream delta-wye HV transformers in the substation have neutral grounding resistors that limit the amps on ground fault until the breaker trips via protective relaying (shielding should carry the fault)
Is it necessary to tie the two underground bonding systems together?
Sent from my iPhone using Tapatalk
The HV substation has its own buried grid installed per IEEE 80. There are HV feeders extending underground from the substation to transformers in the plant. The cables are shielded. The upstream delta-wye HV transformers in the substation have neutral grounding resistors that limit the amps on ground fault until the breaker trips via protective relaying (shielding should carry the fault)
Is it necessary to tie the two underground bonding systems together?
Sent from my iPhone using Tapatalk