Equipotential bonding of perimeter surfaces in accordance
with 680.26(B)(2) shall not be required to be provided
for spas and hot tubs where all of the following
conditions apply:
(1) The spa or hot tub shall be listed as a self-contained spa
for aboveground use.
(2) The spa or hot tub shall not be identified as suitable
only for indoor use.
(3) The installation shall be in accordance with the manufacturer’s
instructions and shall be located on or above
grade.
(4) The top rim of the spa or hot tub shall be at least
710 mm (28 in.) above all perimeter surfaces that are
within 760 mm (30 in.), measured horizontally from
the spa or hot tub. The height of nonconductive external
steps for entry to or exit from the self-contained spa
shall not be used to reduce or increase this rim height
measurement.