equipotential bonding grid

Status
Not open for further replies.

ddzapper

New member
Is the wire mesh used in concrete sidewalks for reinforcing acceptable as the equipotential bonding grid required in NEC 680.26(C) ? (extends 3' beyond the walls of a steel paneled inground pool) This pool is being installed in West Virginia.
 
In my opinion it is a judgement call by the AHJ. The code refers to "structural reinforcing steel", which sounds like rebar to me. I would still pass conductive wire mesh though.
 
I agree with Ryan. Let me add that while art. 680 refers to structural reinforcing steel, 250.52(A)(3) mentions steel reinforcing bars or rods. So, IMO, the wire mesh is acceptable.
 