I build inground gunite swimming pools in the State of Maryland. As I am
sure you are aware, each County can accept or ammend the new code as they
see best for their area. I am having a problem with the City of Frederick,
MD.. They are reading the code to state that rebar, copper, or wire mesh
are required to be attached to the steel grid of the pool structure.
Connected every 12" and tied to the steel with tie wire going under the form
of the pool and out to the decking area. My problem is that when the ground
freezes, it will lift, and by connecting the pool to the decking or the
ground on the exterior of the pool, the pool beam will break. I have passed
many inspections through other Counties by having two #8 bare copper lines
coming off of the bond bar in the pool on opposite ends, and then installing
a #8 bare copper grid 12" on center each way, using copper bugs for all
connections. I have done this for paver decking. For concrete decking, I
have replaced the copper with #3 rebar and installed it 12" on center each
way, clamping the bond wire at both ends of the pool to the grid, using tie
wire to tie the steel grid together since it will be embedded in concrete.
I need you to tell me if this is acceptable. If it is, the Chief Electrical
Inspector will accept your response and allow me to install the grid as
specified above.
At this point the excavation is ready to be gunited, awaiting for approval
from the City since first failed on 8/29. Needless to say, the customer is
the one suffering.
Thanks for reading through this long message.
sure you are aware, each County can accept or ammend the new code as they
see best for their area. I am having a problem with the City of Frederick,
MD.. They are reading the code to state that rebar, copper, or wire mesh
are required to be attached to the steel grid of the pool structure.
Connected every 12" and tied to the steel with tie wire going under the form
of the pool and out to the decking area. My problem is that when the ground
freezes, it will lift, and by connecting the pool to the decking or the
ground on the exterior of the pool, the pool beam will break. I have passed
many inspections through other Counties by having two #8 bare copper lines
coming off of the bond bar in the pool on opposite ends, and then installing
a #8 bare copper grid 12" on center each way, using copper bugs for all
connections. I have done this for paver decking. For concrete decking, I
have replaced the copper with #3 rebar and installed it 12" on center each
way, clamping the bond wire at both ends of the pool to the grid, using tie
wire to tie the steel grid together since it will be embedded in concrete.
I need you to tell me if this is acceptable. If it is, the Chief Electrical
Inspector will accept your response and allow me to install the grid as
specified above.
At this point the excavation is ready to be gunited, awaiting for approval
from the City since first failed on 8/29. Needless to say, the customer is
the one suffering.
Thanks for reading through this long message.