Equipotential Bonding

Status
Not open for further replies.

Eddie King

New member
Is the following statement regarding Equipotential Bonding Grid for vinyl lined polymer swimming pools currently a valid requlation?

"Pools made of non-conductive materials (fiberglass composite, vinyl lined polymer or other non-donductive materials) do not require an equipotential grid that covers the full contour of the bottom and sides of the pool, however an equipotential grid is still required around the perimeter of the pool extending 3' beyond the sides of the pool."

One of our customers in Ohio believes this requlation has changed but I couldn't find specific reference to it in requlation 680.26 NFPA 70.

Thank you,
Eddie King
 
I have it as a TIA- Tentative Interim Amendment. It's been approved by my AHJ. I don't remember how or where I got it. I hope someone else on the site can be of better service. Good luck.
 
Eddie King said:
One of our customers in Ohio believes this requlation has changed but I couldn't find specific reference to it in requlation 680.26 NFPA 70.

Thank you,
Eddie King

I'm not sure what you mean by this ? Changed in what way??
Here is the TIA


Reference: 680.26 TIA 05-2 (NFPA 70) (SC 05-7-15)/Log No. 821) Pursuant to Section 5 of the NFPA Regulations Governing Committee Projects, the National Fire Protection Association has issued the following Tentative Interim Amendment to NFPA 70, National Electrical Code?, 2005 edition. The TIA was processed by the National Electrical Code? Committee, and was issued by the Standards Council on July 29, 2005, with an effective date of August 18, 2005. A Tentative Interim Amendment is tentative because it has not been processed through the entire standards-making procedures. It is interim because it is effective only between editions of the standard. A TIA automatically becomes a proposal of the proponent for the next edition of the standard; as such, it then is subject to all of the procedures of the standards-making process.

1. Revise 680.26 (C) & 680.26 (C)(1) as follows: (C) Equipotential Bonding Grid. The parts specified in 680.26(B) shall be connected to an equipotential bonding grid with a solid copper conductor, insulated, covered, or bare, not smaller than 8 AWG or rigid metal conduit of brass or other identified corrosion-resistant metal conduit. Connection shall be made by exothermic welding or by listed pressure connectors or clamps that are labeled as being suitable for the purpose and are of stainless steel, brass, copper, or copper alloy. The equipotential bonding grid shall conform to the contours of the pool and shall extend within or under paved walking surfaces for 1 m (3 ft) horizontally beyond the inside walls of the pool and shall be permitted to be any of the following: Exception: The equipotential bonding grid shall not be required to be installed under the bottom of or vertically along the walls of vinyl lined polymer wall, fiberglass composite, or other pools constructed of nonconductive materials. Any metal parts of the pool, including metal structural supports, shall be bonded in accordance with 680.26(B). For the purposes of this section, poured concrete, pneumatically applied (sprayed) concrete, and concrete block, with painted or plastered coatings, shall be considered conductive material. (1) Structural Reinforcing Steel. The structural reinforcing steel of a concrete pool or deck where the reinforcing rods are bonded together by the usual steel tie wires or the equivalent. Where deck reinforcing steel is not an integral part of the pool, the deck reinforcing steel shall be bonded to other parts of the bonding grid using a minimum 8 AWG solid copper conductor. Connection shall be per 680.26(D).

Copyright ? 2005 All Rights Reserved NATIONAL FIRE PROTECTION ASSOCIATION
__________________
 
I also found this,.. I hope it helps

Ohio never recognizes TIAs but 680.26(C) is so screwed up that Ohio added the TIA into the state building code. I don't know if they added it word for word because we still haven't seen the new building code section. But I know the requirement to add a grid under a nonmetalic inground is gone.

The three foot bonding of the paved area around the pool is still required.

David
__________________
Inspector
Medina County Ohio
&
PSECI
 
new_ani.gif
SWIMMING POOLS

NFPA TIA70-05-2
 