When does a pool require an equipotential grid? When does it not?
Pretty much always if it is an in ground pool.Isnt there an alternate means that doesnt require a grid but only a number 8 contoured to the pool?
When is the grid itself required?
680.26 Equipotential Bonding
(A) Performance. The equipotential bonding required by
this section shall be installed to reduce voltage gradients in
the pool area.
(B) Bonded Parts. The parts specified in 680.26(B)(1)
through (B)(7) shall be bonded together.....
(1) Conductive Pool Shells. Bonding to conductive pool
shells shall be provided as specified in 680.26(B)(1)(a) or
(B)(1)(b). Poured concrete, pneumatically applied or
sprayed concrete, and concrete block with painted or plas-
tered coatings shall all be considered conductive....
(a) Structural Reinforcing Steel. Unencapsulated struc-
tural reinforcing steel shall be bonded together by steel tie
wires or the equivalent. Where structural reinforcing steel is
encapsulated in a nonconductive compound, a copper con-
ductor grid shall be installed in accordance with 680.26(B)
(1)(b).
(2) Perimeter Surfaces. The perimeter surface shall ex-
tend for 1 m (3 ft) horizontally beyond the inside walls of
the pool and shall include unpaved surfaces, as well as
poured concrete surfaces and other types of paving
Ok so all in ground pools require a 3 ft grid around them?
The code book is not specific about this at all.
Equipotential Bonding.
I think you need to clarify what you mean when you say Equipotential Bonding “Grid”
The pool needs equipotential bonding the perimeter surface needs bonded.
“Vinyl liners and fiberglass composite shells shall be considered to be nonconductive materials.
When a in ground pool has a vinyl liner and the pool structure itself is considered non- conductive the pool structure itself has no requirement to be bonded to the Equipotential bonding system for the pool.
680.26( C ) applies
Equipotential Bonding.
I think you need to clarify what you mean when you say Equipotential Bonding “Grid”
The pool needs equipotential bonding the perimeter surface needs bonded.
“Vinyl liners and fiberglass composite shells shall be considered to be nonconductive materials.
When a in ground pool has a vinyl liner and the pool structure itself is considered non- conductive the pool structure itself has no requirement to be bonded to the Equipotential bonding system for the pool.
680.26( C ) applies
yes pool water needs bonded,
most often done through metal elements part of the pool, ladders, handrails, even metal trim rings for underwater lighting.