2005 NEC 680.26(C) and here is Washington State take on the issue.
NEC 680.26(C) describes the specific requirements for the equipotential bonding grid for pools with
paved walking areas (e.g. concrete, tiles, pavers, wood, etc.). The grid must extend from the inside walls
of the pool at least 3? under the walking area. Depending on the type of pool construction, you have three
options for constructing a grid under the walking area:
Structural reinforcing steel ? This option can only be used with a steel reinforced concrete pool.
Uninsulated steel structural reinforcing bars may be used to make a grid if they are bonded together with
steel tie wire or equivalent.
Bolted/welded metal pools ? The wall of a bolted or welded metal pool may be used as the grid.
Alternate means ? This option can be used when a deck media exists (e.g. concrete, pavers, wood deck,
etc.). The grid must be made of a minimum #8 solid copper conductor that is bonded at all crossing
points. The grid must cover the entire area from the contour of the pool and extending at least 3? under
the pool deck. The grid must be made in a 1? x 1? perpendicular pattern ? 4?. The grid must be secured
within or under the pool and deck media.
The 2005 NEC does not have specific grid installation methods for a pool with no paved walking area
(e.g. grass, gravel, etc.). The lack of description does not eliminate the requirement for a grid. For the
perimeter area around these pools, L&I inspectors will accept a single, minimum #8 solid copper,
conductor that is installed between 18? and 24? of the contour of the inside wall of the pool and is buried
under the perimeter surface at least 6? below grade. Only listed splices will be accepted.
All metal parts requiring bonding in NEC 680.26(B) must be bonded to the equipotential bonding grid.
The 2008 NEC modifies some of these requirements. They will be covered in a future newsletter
As my boss says "It is all black and white."
But IMO the exposed rebar is no good.