I'm dealing with a patient care facility and below based on Florida code FBC. 451.3.10.4 is a requirement that i need a clarification on in patient rooms. I'm a little confused on how to accomplish this? Does this mean that hospital grade type receptacle is required and does that cover it? Or does every patient room require a grounding busbar. Any clarifiaction on this would be appreciated in the (patient areas) and not at service location. Thank you
451.3.10.4
There shall be documentation for equipotential grounding in all patient care areas, building service ground electrode systems, and special systems such as fire alarm, nurse call, paging, generator, emergency power and breaker coordination.
451.3.10.4
There shall be documentation for equipotential grounding in all patient care areas, building service ground electrode systems, and special systems such as fire alarm, nurse call, paging, generator, emergency power and breaker coordination.