Has anyone heard of a proposal or the rumors of the code making panel cloning 682.33 to 680 part IV.?
The requirement already exist682.33 Equipotential Planes and Bonding of Equipment Planes.
An equipotential plane shall be installed where required in this section to mitigate step and touch voltages at electrical equipment.
(A) Areas Requiring Equipotential Planes. Equipotential planes shall be installed adjacent to all outdoor service equipment or disconnecting means that control equipment in or on water, that have a metallic enclosure and controls accessible to personnel, and that are likely to become energized. The equipotential plane shall encompass the area around the equipment and shall extend from the area directly below the equipment out not less than 900 mm (36 in.) in all directions from which a person would be able to stand and come in contact with the equipment.
A box of dirt is a poor conductor. But a planet's worth of dirt is an extraordinarily good conductor.Originally posted by peter d: Dirt is a poor conductor, or put another way, an unpredictable conductor.