Baeljb
Member
- Location
- Denver, CO, USA
I am troubleshooting a flickering light problem at a one-year old residence and would appreciate suggestions from members. The residence has 70+ assorted electronic dimmers serving a variety of lights including LED, incandescent, etc. It has a 1000amp. 120/240 single-phase service. At lower output (50%) the lights will strobe multiple times per second, for hours at a time. We, and the dimmer manufacturer, have done extensive testing with high-end meters and storage oscilloscopes. We have concluded that there is erratic (shifting from cycle-to-cycle) voltage distortion on the utility feed. RMS voltage is jumping 0.2 volts per cycle. It is present when all loads in the home are off and also present at neighbor’s homes and a local business two miles away. The distortion is present at the zero-crossing point. The dimmer manufacturer says that they reference the zero-crossing point to adjust output voltage. They do not have a fix. I would normally expect to see Vthd on the service but not have it shifting once large non-linear loads on the distribution stabilize. Vthd is less than 4% and within the utility standards. We are attempting to pressure the reluctant utility into investigate their feeder loads and would appreciate any feedback on possible causes. I should mention that once the residence is transferred to its emergency generator, the flickering disappears. Thank you!