I don't see any requirement for an Energy Storage System (ESS) to comply with the Rapid Shutdown requirements of 2017 section 690.12...(one purpose of the ESS is to supply power on AC power loss, right.)
I'm trying to evaluate what first responders need to do to cut ALL power inside a building during a emergency. (Rapidly)
Looks like the 706.11 Directory requirement is the only guide for the emergency responder. This directory will have to include the required 706.7 ESS Disconnecting Means, which could be inside the building anywhere.
Any local requirement out there yet for outside disconnects of Energy Storage Systems?
I'm trying to evaluate what first responders need to do to cut ALL power inside a building during a emergency. (Rapidly)
Looks like the 706.11 Directory requirement is the only guide for the emergency responder. This directory will have to include the required 706.7 ESS Disconnecting Means, which could be inside the building anywhere.
Any local requirement out there yet for outside disconnects of Energy Storage Systems?