Essential electrical system wiring methods

Status
Not open for further replies.

mcgjosj

New User
Location
MN
Occupation
Electrician
I am in a rabbit hole and could use some clarification. Are there any listed cables that can be used on the essential electrical system for hospitals. I have been looking on the manufacture's websites and it is not very clear whether you can or can't. I only found one Southwire cable that said you couldn't use it. FMC is only good for 6'. Looking for approved cable's for fishing applications longer than 6' on emergency power. Please help!

Thanks
 
517.30(C)(3)(3)(c) allows fishing listed HCFC into existing walls.
Actually if it's outside a patient care area any listed cable can be fished into existing walls.

Roger
 