wipeflusher
- Essexville, Michigan USA
Greetings to all. My first time here, so I'll try to be articulate:
I work at a skilled nursing care facility. My service to the facility is 480v, 800 amps. Before I got here, there was one 250kva generator supplying the Essential system power to the building. Since that time, we have replaced that with 2) 500kva generators, and also added a separate (fourth) transfer switch that connects "Normal Power" to the generator back up. So, I now have 100% of the building backed up on generator power. (the normal power xfer switch is time delayed 10 seconds).
I'm wanting to re-do power to our Laundry facility, which the equipment (washers, dryers, linen folders, etc.) has been, and still is on the Equipment branch of the Essential Systems. I was hoping to supply a new 480 volt feeder from the Normal Power switchgear to the Laundry Room, transform it down to 208/120v and transfer the existing branch circuits from an old panel to a new one located in another area of the Laundry Room. I asked my electrical engineer (we're doing an extensive remodeling project) if I could take that feeder load OFF of the Equipment branch and feed it through Normal Power now, since the building is now basically 100% backed up. Even though he didn't have anything to back up his opinion, he thought we should leave it on the Equipment branch.
I know that NEC 517.34(B) contains a list of specific equipment permitted to be connected to the equipment system (item 8), referring to non-specific and generalized, where 517.30 (B)(5) requires equipment to be specifically named and served by their own transfer switches. If you get into NFPA 99 (Health Care Facilities), Section 3.4.2.2.3 (e), the appendix has this commentary:
"Consideration should be given to selected equipment in kitchens, laundries, and radiology rooms and to selected central refrigeration." It goes on to address handling heavy loads, etc.
In essence, there's a lot in the codes talking about what ADDITIONAL loads COULD be added to the Equipment branch, but again, we're talking about a facility that only has generator back up on the Essential system and not the entire building like we are now. A lot of focus is on making sure this extra equipment is on an additional transfer device. I see the new Normal Power Transfer Switch we installed as such an additional device. How do I address code adherence to a building that's 100% backed up?