To expand a little on what Iwire said, isolated ground is not isolated from the building grounding system, where it must terminate typically at the service equipment.
It is isolated from other equipment grounding conductors all the way from service to the outlet. The isolated grounding conductor passes through all raceways, junction boxes panelboards, etc. with no connection to these enclosures and is in addition to the required equipment grounding conductor required to bond these enclosures or other non isolated grounded items.
Do not confuse isolated ground terminology to running a wire from the IG receptacle to a ground rod (and nothing else) like many seem to do.