Collin
Member
- Location
- Huntington, WV
- Occupation
- Electrical Engineer
I have been asked to give an evaluation of an existing power supply so that a client can know what amount of load can be added to it(it is a warehouse with some office space). For loads with known FLA, I do the proper calculation, however, for unknown loads I calculated "worst case" with each at 80% of the breaker amps. This obviously inflates my load beyond what it says the panels are rated for(for all but one panel). Without redoing a load calculation for all the lighting, receptacles, heaters, etcetera, does the NEC allow me to make assumptions about these loads?
I have read into NEC 220 a little and have seen the values of 180VA per receptacle and that Warehouse lighting is 1/4VA per Sq. Ft., but these are 20A receptacles and lighting circuits just labeled, "receptacles" and "warehouse lights," no idea how many are on each circuit.
General information: Some lighting is on 277V(480/277V) and the majority is on 120(208/120V), all receptacles are 120V, warehouse is 51,200 sq. ft., office is 2,500 sq. ft.
My spreadsheet calcs: I'm multiplying and dividing by 1000 for KVA since it looks nicer in the spreadsheet
3p KVA = 1.73*VLL*IL/1000
2p KVA = VLL*IL/1000
1p KVA = VLN*IL/1000
Add up all the KVA and find the amps = (KVA*1000)/(VLL*1.73)
I have read into NEC 220 a little and have seen the values of 180VA per receptacle and that Warehouse lighting is 1/4VA per Sq. Ft., but these are 20A receptacles and lighting circuits just labeled, "receptacles" and "warehouse lights," no idea how many are on each circuit.
General information: Some lighting is on 277V(480/277V) and the majority is on 120(208/120V), all receptacles are 120V, warehouse is 51,200 sq. ft., office is 2,500 sq. ft.
My spreadsheet calcs: I'm multiplying and dividing by 1000 for KVA since it looks nicer in the spreadsheet
3p KVA = 1.73*VLL*IL/1000
2p KVA = VLL*IL/1000
1p KVA = VLN*IL/1000
Add up all the KVA and find the amps = (KVA*1000)/(VLL*1.73)