William Teller
New User
- Texas
- Electrical Engineer
I occasionally design renovations to existing facilities. Sometimes I have accurate as-built drawings that show the existing load of a panel and sometimes not. If you count 80 percent of the capacity of each branch breaker that is connected, you often come up with an existing calculated load that is far greater than the main breaker of the panel. Now if you have a main panel and disconnect that is rated at 1000A and have 4 sub distribution panels that are 600A and the load is more or less evenly distributed, then I would think that you could divide the peak demand load (in this case 425A at the service.) by 4 to estimate how much load is on each sub distribution panel. But, I was told you can not do this by a senior electrical engineer. I was told that if you add load to a panel, even if it is say 13 amps on an unused 20A 120A/1P breaker you would have to assume: 1) all of the peak demand load on the service is on the distribution panel that feeds that panel and that most of that load is on the branch panel you are updating. Or, 2) you have do a load analysis of that upstream distribution panel and every panel that is fed from it. Does that seem reasonable to you.
FYI, doing a 30 day load measurement is often not practical and the same senior engineer says that you have to do a load measurement of the panel and upstream distribution panel for a whole year to have meaningful results.
I appreciate any wisdom on this mater.