I do believe they are based on an IEC standard. Some of the ratings you see on IEC equipment that is used in the US may give you clues as to what may be popular sizes used there. I know 16 amps is one of those sizes.What are the typical outlet amp ratings in the European Union for 1~ 220-240VAC? For example, in the US you can readily find 15 and 20A outlets. I've heard in Europe it is 16A...is that true? What other amp ratings are available in 220-240VAC 1~?
What are the typical outlet amp ratings in the European Union for 1~ 220-240VAC? For example, in the US you can readily find 15 and 20A outlets. I've heard in Europe it is 16A...is that true? What other amp ratings are available in 220-240VAC 1~?
What are the typical outlet amp ratings in the European Union for 1~ 220-240VAC? For example, in the US you can readily find 15 and 20A outlets. I've heard in Europe it is 16A...is that true? What other amp ratings are available in 220-240VAC 1~?
In UK it's 13A. That's it.What are the typical outlet amp ratings in the European Union for 1~ 220-240VAC? For example, in the US you can readily find 15 and 20A outlets. I've heard in Europe it is 16A...is that true? What other amp ratings are available in 220-240VAC 1~?
In UK it's 13A. That's it.
I don't know about other European countries.
You have to have other receptacles for heavier loads, or is there no quick unplugging of anything but items that use that particular receptacle. There about has to be some cord and plug type of assemblies for some industrial applications or else you need an electrician for every frequent interchange situation that we often use higher amperage receptacles for around these parts. The user doesn't need to know how to connect it, just how to push the plug into the receptacle.
For single phase domestic, that's it. There are no others. At 13A it is about 3kW for resistive.You have to have other receptacles for heavier loads, or is there no quick unplugging of anything but items that use that particular receptacle.
Yes, for industrial use there are 3-phase plugs and sockets.There about has to be some cord and plug type of assemblies for some industrial applications or else you need an electrician for every frequent interchange situation that we often use higher amperage receptacles for around these parts. The user doesn't need to know how to connect it, just how to push the plug into the receptacle.
I think having just one voltage has merits.Now I can see that being the only receptacle used in the typical household. Other than ranges and clothes dryers most of equipment used in the typical US household would only require one receptacle type if there was only one common utilization voltage like you have.
For single phase domestic, that's it. There are no others. At 13A it is about 3kW for resistive.
Yes, for industrial use there are 3-phase plugs and sockets.
View attachment 9591
That's for 32A, 400V, 3-phase+n
I think having just one voltage has merits.
Does the "n" pin supply the equipment grounding condutor?... Yes, for industrial use there are 3-phase plugs and sockets.
View attachment 9591
That's for 32A, 400V, 3-phase+n ....
Not to mention the loss of revenue for electricians having to find lost neutrals!But think of all the money the device manufacturers make. If you made it so there was only one product to use - that is just anti-Americanism at its finest:happyyes:
That's right, the more complicated we can keep things the more true the "professional" title becomes:happyyes:Not to mention the loss of revenue for electricians having to find lost neutrals!
Or the replacement sales of kit that got hit by the more than intended 120V.
Horrifying thoughts....hmy:
Does the "n" pin supply the equipment grounding condutor?
Or does it not have an equipment grounding conductor?
ice
The n is the neutral. It is usually earthed (grounded) back at the supply transformer.
It's a current carrying conductor.maybe the better question (and probably what iceworm was after) is can the neutral carry current for line to neutral loads or is it for grounding purposes only,
It's a current carrying conductor.
Usually, in my experience, a separate conductor is run for that.And it also povides an equipotential equipment bonding conductor?
ice
Usually, in my experience, a separate conductor is run for that.Adrian (another Brit here) has given examples where sometimes the neutral is grounded at various points.
I'll try to dig up some pics.